Shown is the 1993 resistor pack. Testing is the same for newer model units with more speeds - 4 resistor coils and the different design of only 1 Thermal fuse. Good pic to post, AK.
No you can't tell by looking at them as corrosion makes it look bad but it is good.
1993 is behind glove box and a relay pack on top of the HVAC unit. The bolts require a wrench and time to get the stubborn tight fit one out.
As the other threads show check the main HVAC power connector for melting and add a extra ground to the blower motor.